Network Working Group J. Case, Editor

Request for Comments: 1628 SNMP Research, Incorporated

Category: Standards Track May 1994

UPS Management Information Base

Status of this Memo

This document specifies an Internet standards track protocol for the

Internet community, and requests discussion and suggestions for

improvements. Please refer to the current edition of the "Internet

Official Protocol Standards" (STD 1) for the standardization state

and status of this protocol. Distribution of this memo is unlimited.

Table of Contents

1. IntrodUCtion .............................................. 1

2. The SNMPv2 Network Management Framework ................... 2

2.1 Object Definitions ....................................... 2

3. Overview .................................................. 2

4. Definitions ............................................... 3

4.1 The Device Identification Group........................... 4

4.2 The Battery Group ........................................ 5

4.3 The Input Group .......................................... 7

4.4 The Output Group ......................................... 9

4.5 The Bypass Group ......................................... 12

4.6 The Alarm Group .......................................... 13

4.7 The Test Group ........................................... 19

4.8 The Control Group ........................................ 23

4.9 The Configuration Group .................................. 26

5. Acknowledgements .......................................... 43

6. References ................................................ 44

7. Security Considerations ................................... 45

8. Author's Address .......................................... 45

1. Introduction

This memo defines a portion of the Management Information Base (MIB)

for use with network management protocols in the Internet community.

In particular, it defines objects for managing uninterruptible power

supply (UPS) systems.

2. The SNMPv2 Network Management Framework

The SNMPv2 Network Management Framework consists of four major

components. They are:

o RFC1442 which defines the SMI, the mechanisms used for

describing and naming objects for the purpose of management.

o STD 17, RFC1213 defines MIB-II, the core set of managed

objects for the Internet suite of protocols.

o RFC1445 which defines the administrative and other

architectural ASPects of the framework.

o RFC1448 which defines the protocol used for network Access

to managed objects.

The Framework permits new objects to be defined for the purpose of

eXPerimentation and evaluation.

2.1. Object Definitions

Managed objects are accessed via a virtual information store, termed

the Management Information Base or MIB. Objects in the MIB are

defined using the subset of Abstract Syntax Notation One (ASN.1)

defined in the SMI. In particular, each object type is named by an

OBJECT IDENTIFIER, an administratively assigned name. The object

type together with an object instance serves to uniquely identify a

specific instantiation of the object. For human convenience, we

often use a textual string, termed the descriptor, to refer to the

object type.

3. Overview

This document defines the managed objects for Uninterruptible Power

Supplies which are to be manageable via the Simple Network Management

Protocol (SNMP).

4. Definitions

UPS-MIB DEFINITIONS ::= BEGIN

IMPORTS

MODULE-IDENTITY, OBJECT-TYPE, NOTIFICATION-TYPE,

OBJECT-IDENTITY, Counter32, Gauge32, Integer32

FROM SNMPv2-SMI

DisplayString, TimeStamp, TimeInterval, TestAndIncr,

AutonomousType

FROM SNMPv2-TC

MODULE-COMPLIANCE, OBJECT-GROUP

FROM SNMPv2-CONF;

upsMIB MODULE-IDENTITY

LAST-UPDATED "9402230000Z"

ORGANIZATION "IETF UPS MIB Working Group"

CONTACT-INFO

" Jeffrey D. Case

Postal: SNMP Research, Incorporated

3001 Kimberlin Heights Road

Knoxville, TN 37920

US

Tel: +1 615 573 1434

Fax: +1 615 573 9197

E-mail: case@snmp.com"

DESCRIPTION

"The MIB module to describe Uninterruptible Power

Supplies."

::= { mib-2 33 }

PositiveInteger ::= TEXTUAL-CONVENTION

DISPLAY-HINT "d"

STATUS current

DESCRIPTION

"This data type is a non-zero and non-negative value."

SYNTAX INTEGER (1..2147483647)

NonNegativeInteger ::= TEXTUAL-CONVENTION

DISPLAY-HINT "d"

STATUS current

DESCRIPTION

"This data type is a non-negative value."

SYNTAX INTEGER (0..2147483647)

upsObjects OBJECT IDENTIFIER ::= { upsMIB 1 }

--

-- The Device Identification group.

-- All objects in this group except for upsIdentName and

-- upsIdentAttachedDevices are set at device initialization

-- and remain static.

--

upsIdent OBJECT IDENTIFIER ::= { upsObjects 1 }

upsIdentManufacturer OBJECT-TYPE

SYNTAX DisplayString (SIZE (0..31))

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The name of the UPS manufacturer."

::= { upsIdent 1 }

upsIdentModel OBJECT-TYPE

SYNTAX DisplayString (SIZE (0..63))

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The UPS Model designation."

::= { upsIdent 2 }

upsIdentUPSSoftwareVersion OBJECT-TYPE

SYNTAX DisplayString (SIZE (0..63))

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The UPS firmware/software version(s). This variable

may or may not have the same value as

upsIdentAgentSoftwareVersion in some implementations."

::= { upsIdent 3 }

upsIdentAgentSoftwareVersion OBJECT-TYPE

SYNTAX DisplayString (SIZE (0..63))

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The UPS agent software version. This variable may or

may not have the same value as

upsIdentUPSSoftwareVersion in some implementations."

::= { upsIdent 4 }

upsIdentName OBJECT-TYPE

SYNTAX DisplayString (SIZE(0..63))

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"A string identifying the UPS. This object should be

set by the administrator."

::= { upsIdent 5 }

upsIdentAttachedDevices OBJECT-TYPE

SYNTAX DisplayString (SIZE(0..63))

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"A string identifying the devices attached to the

output(s) of the UPS. This object should be set by

the administrator."

::= { upsIdent 6 }

--

-- Battery Group

--

upsBattery OBJECT IDENTIFIER ::= { upsObjects 2 }

upsBatteryStatus OBJECT-TYPE

SYNTAX INTEGER {

unknown(1),

batteryNormal(2),

batteryLow(3),

batteryDepleted(4)

}

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The indication of the capacity remaining in the UPS

system's batteries. A value of batteryNormal

indicates that the remaining run-time is greater than

upsConfigLowBattTime. A value of batteryLow indicates

that the remaining battery run-time is less than or

equal to upsConfigLowBattTime. A value of

batteryDepleted indicates that the UPS will be unable

to sustain the present load when and if the utility

power is lost (including the possibility that the

utility power is currently absent and the UPS is

unable to sustain the output)."

::= { upsBattery 1 }

upsSecondsOnBattery OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "seconds"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"If the unit is on battery power, the elapsed time

since the UPS last switched to battery power, or the

time since the network management subsystem was last

restarted, whichever is less. Zero shall be returned

if the unit is not on battery power."

::= { upsBattery 2 }

upsEstimatedMinutesRemaining OBJECT-TYPE

SYNTAX PositiveInteger

UNITS "minutes"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"An estimate of the time to battery charge depletion

under the present load conditions if the utility power

is off and remains off, or if it were to be lost and

remain off."

::= { upsBattery 3 }

upsEstimatedChargeRemaining OBJECT-TYPE

SYNTAX INTEGER (0..100)

UNITS "percent"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"An estimate of the battery charge remaining expressed

as a percent of full charge."

::= { upsBattery 4 }

upsBatteryVoltage OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 Volt DC"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The magnitude of the present battery voltage."

::= { upsBattery 5 }

upsBatteryCurrent OBJECT-TYPE

SYNTAX Integer32

UNITS "0.1 Amp DC"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present battery current."

::= { upsBattery 6 }

upsBatteryTemperature OBJECT-TYPE

SYNTAX Integer32

UNITS "degrees Centigrade"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The ambient temperature at or near the UPS Battery

casing."

::= { upsBattery 7 }

--

-- Input Group

--

upsInput OBJECT IDENTIFIER ::= { upsObjects 3 }

upsInputLineBads OBJECT-TYPE

SYNTAX Counter32

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"A count of the number of times the input entered an

out-of-tolerance condition as defined by the

manufacturer. This count is incremented by one each

time the input transitions from zero out-of-tolerance

lines to one or more input lines out-of-tolerance."

::= { upsInput 1 }

upsInputNumLines OBJECT-TYPE

SYNTAX NonNegativeInteger

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The number of input lines utilized in this device.

This variable indicates the number of rows in the

input table."

::= { upsInput 2 }

upsInputTable OBJECT-TYPE

SYNTAX SEQUENCE OF UpsInputEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"A list of input table entries. The number of entries

is given by the value of upsInputNumLines."

::= { upsInput 3 }

upsInputEntry OBJECT-TYPE

SYNTAX UpsInputEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"An entry containing information applicable to a

particular input line."

INDEX { upsInputLineIndex }

::= { upsInputTable 1 }

UpsInputEntry ::= SEQUENCE {

upsInputLineIndex PositiveInteger,

upsInputFrequency NonNegativeInteger,

upsInputVoltage NonNegativeInteger,

upsInputCurrent NonNegativeInteger,

upsInputTruePower NonNegativeInteger

}

upsInputLineIndex OBJECT-TYPE

SYNTAX PositiveInteger

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"The input line identifier."

::= { upsInputEntry 1 }

upsInputFrequency OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 Hertz"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present input frequency."

::= { upsInputEntry 2 }

upsInputVoltage OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The magnitude of the present input voltage."

::= { upsInputEntry 3 }

upsInputCurrent OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 RMS Amp"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The magnitude of the present input current."

::= { upsInputEntry 4 }

upsInputTruePower OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "Watts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The magnitude of the present input true power."

::= { upsInputEntry 5 }

--

-- The Output group.

--

upsOutput OBJECT IDENTIFIER ::= { upsObjects 4 }

upsOutputSource OBJECT-TYPE

SYNTAX INTEGER {

other(1),

none(2),

normal(3),

bypass(4),

battery(5),

booster(6),

reducer(7)

}

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present source of output power. The enumeration

none(2) indicates that there is no source of output

power (and therefore no output power), for example,

the system has opened the output breaker."

::= { upsOutput 1 }

upsOutputFrequency OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 Hertz"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present output frequency."

::= { upsOutput 2 }

upsOutputNumLines OBJECT-TYPE

SYNTAX NonNegativeInteger

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The number of output lines utilized in this device.

This variable indicates the number of rows in the

output table."

::= { upsOutput 3 }

upsOutputTable OBJECT-TYPE

SYNTAX SEQUENCE OF UpsOutputEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"A list of output table entries. The number of

entries is given by the value of upsOutputNumLines."

::= { upsOutput 4 }

upsOutputEntry OBJECT-TYPE

SYNTAX UpsOutputEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"An entry containing information applicable to a

particular output line."

INDEX { upsOutputLineIndex }

::= { upsOutputTable 1 }

UpsOutputEntry ::= SEQUENCE {

upsOutputLineIndex PositiveInteger,

upsOutputVoltage NonNegativeInteger,

upsOutputCurrent NonNegativeInteger,

upsOutputPower NonNegativeInteger,

upsOutputPercentLoad INTEGER

}

upsOutputLineIndex OBJECT-TYPE

SYNTAX PositiveInteger

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"The output line identifier."

::= { upsOutputEntry 1 }

upsOutputVoltage OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present output voltage."

::= { upsOutputEntry 2 }

upsOutputCurrent OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 RMS Amp"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present output current."

::= { upsOutputEntry 3 }

upsOutputPower OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "Watts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present output true power."

::= { upsOutputEntry 4 }

upsOutputPercentLoad OBJECT-TYPE

SYNTAX INTEGER (0..200)

UNITS "percent"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The percentage of the UPS power capacity presently

being used on this output line, i.e., the greater of

the percent load of true power capacity and the

percent load of VA."

::= { upsOutputEntry 5 }

--

-- The Bypass group.

--

upsBypass OBJECT IDENTIFIER ::= { upsObjects 5 }

upsBypassFrequency OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 Hertz"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present bypass frequency."

::= { upsBypass 1 }

upsBypassNumLines OBJECT-TYPE

SYNTAX NonNegativeInteger

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The number of bypass lines utilized in this device.

This entry indicates the number of rows in the bypass

table."

::= { upsBypass 2 }

upsBypassTable OBJECT-TYPE

SYNTAX SEQUENCE OF UpsBypassEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"A list of bypass table entries. The number of

entries is given by the value of upsBypassNumLines."

::= { upsBypass 3 }

upsBypassEntry OBJECT-TYPE

SYNTAX UpsBypassEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"An entry containing information applicable to a

particular bypass input."

INDEX { upsBypassLineIndex }

::= { upsBypassTable 1 }

UpsBypassEntry ::= SEQUENCE {

upsBypassLineIndex PositiveInteger,

upsBypassVoltage NonNegativeInteger,

upsBypassCurrent NonNegativeInteger,

upsBypassPower NonNegativeInteger

}

upsBypassLineIndex OBJECT-TYPE

SYNTAX PositiveInteger

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"The bypass line identifier."

::= { upsBypassEntry 1 }

upsBypassVoltage OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present bypass voltage."

::= { upsBypassEntry 2 }

upsBypassCurrent OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 RMS Amp"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present bypass current."

::= { upsBypassEntry 3 }

upsBypassPower OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "Watts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present true power conveyed by the bypass."

::= { upsBypassEntry 4 }

--

-- The Alarm group.

--

upsAlarm OBJECT IDENTIFIER ::= { upsObjects 6 }

upsAlarmsPresent OBJECT-TYPE

SYNTAX Gauge32

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The present number of active alarm conditions."

::= { upsAlarm 1 }

upsAlarmTable OBJECT-TYPE

SYNTAX SEQUENCE OF UpsAlarmEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"A list of alarm table entries. The table contains

zero, one, or many rows at any moment, depending upon

the number of alarm conditions in effect. The table

is initially empty at agent startup. The agent

creates a row in the table each time a condition is

detected and deletes that row when that condition no

longer pertains. The agent creates the first row with

upsAlarmId equal to 1, and increments the value of

upsAlarmId each time a new row is created, wrapping to

the first free value greater than or equal to 1 when

the maximum value of upsAlarmId would otherwise be

exceeded. Consequently, after multiple operations,

the table may become sparse, e.g., containing entries

for rows 95, 100, 101, and 203 and the entries should

not be assumed to be in chronological order because

upsAlarmId might have wrapped.

Alarms are named by an AutonomousType (OBJECT

IDENTIFIER), upsAlarmDescr, to allow a single table to

reflect well known alarms plus alarms defined by a

particular implementation, i.e., as documented in the

private enterprise MIB definition for the device. No

two rows will have the same value of upsAlarmDescr,

since alarms define conditions. In order to meet this

requirement, care should be taken in the definition of

alarm conditions to insure that a system cannot enter

the same condition multiple times simultaneously.

The number of rows in the table at any given time is

reflected by the value of upsAlarmsPresent."

::= { upsAlarm 2 }

upsAlarmEntry OBJECT-TYPE

SYNTAX UpsAlarmEntry

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"An entry containing information applicable to a

particular alarm."

INDEX { upsAlarmId }

::= { upsAlarmTable 1 }

UpsAlarmEntry ::= SEQUENCE {

upsAlarmId PositiveInteger,

upsAlarmDescr AutonomousType,

upsAlarmTime TimeStamp

}

upsAlarmId OBJECT-TYPE

SYNTAX PositiveInteger

MAX-ACCESS not-accessible

STATUS current

DESCRIPTION

"A unique identifier for an alarm condition. This

value must remain constant."

::= { upsAlarmEntry 1 }

upsAlarmDescr OBJECT-TYPE

SYNTAX AutonomousType

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"A reference to an alarm description object. The

object referenced should not be accessible, but rather

be used to provide a unique description of the alarm

condition."

::= { upsAlarmEntry 2 }

upsAlarmTime OBJECT-TYPE

SYNTAX TimeStamp

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The value of sysUpTime when the alarm condition was

detected. If the alarm condition was detected at the

time of agent startup and presumably existed before

agent startup, the value of upsAlarmTime shall equal

0."

::= { upsAlarmEntry 3 }

--

-- Well known alarm conditions.

--

upsWellKnownAlarms OBJECT IDENTIFIER ::= { upsAlarm 3 }

upsAlarmBatteryBad OBJECT-IDENTITY

STATUS current

DESCRIPTION

"One or more batteries have been determined to require

replacement."

::= { upsWellKnownAlarms 1 }

upsAlarmOnBattery OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The UPS is drawing power from the batteries."

::= { upsWellKnownAlarms 2 }

upsAlarmLowBattery OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The remaining battery run-time is less than or equal

to upsConfigLowBattTime."

::= { upsWellKnownAlarms 3 }

upsAlarmDepletedBattery OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The UPS will be unable to sustain the present load

when and if the utility power is lost."

::= { upsWellKnownAlarms 4 }

upsAlarmTempBad OBJECT-IDENTITY

STATUS current

DESCRIPTION

"A temperature is out of tolerance."

::= { upsWellKnownAlarms 5 }

upsAlarmInputBad OBJECT-IDENTITY

STATUS current

DESCRIPTION

"An input condition is out of tolerance."

::= { upsWellKnownAlarms 6 }

upsAlarmOutputBad OBJECT-IDENTITY

STATUS current

DESCRIPTION

"An output condition (other than OutputOverload) is

out of tolerance."

::= { upsWellKnownAlarms 7 }

upsAlarmOutputOverload OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The output load exceeds the UPS output capacity."

::= { upsWellKnownAlarms 8 }

upsAlarmOnBypass OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The Bypass is presently engaged on the UPS."

::= { upsWellKnownAlarms 9 }

upsAlarmBypassBad OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The Bypass is out of tolerance."

::= { upsWellKnownAlarms 10 }

upsAlarmOutputOffAsRequested OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The UPS has shutdown as requested, i.e., the output

is off."

::= { upsWellKnownAlarms 11 }

upsAlarmUpsOffAsRequested OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The entire UPS has shutdown as commanded."

::= { upsWellKnownAlarms 12 }

upsAlarmChargerFailed OBJECT-IDENTITY

STATUS current

DESCRIPTION

"An uncorrected problem has been detected within the

UPS charger subsystem."

::= { upsWellKnownAlarms 13 }

upsAlarmUpsOutputOff OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The output of the UPS is in the off state."

::= { upsWellKnownAlarms 14 }

upsAlarmUpsSystemOff OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The UPS system is in the off state."

::= { upsWellKnownAlarms 15 }

upsAlarmFanFailure OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The failure of one or more fans in the UPS has been

detected."

::= { upsWellKnownAlarms 16 }

upsAlarmFuseFailure OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The failure of one or more fuses has been detected."

::= { upsWellKnownAlarms 17 }

upsAlarmGeneralFault OBJECT-IDENTITY

STATUS current

DESCRIPTION

"A general fault in the UPS has been detected."

::= { upsWellKnownAlarms 18 }

upsAlarmDiagnosticTestFailed OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The result of the last diagnostic test indicates a

failure."

::= { upsWellKnownAlarms 19 }

upsAlarmCommunicationsLost OBJECT-IDENTITY

STATUS current

DESCRIPTION

"A problem has been encountered in the communications

between the agent and the UPS."

::= { upsWellKnownAlarms 20 }

upsAlarmAwaitingPower OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The UPS output is off and the UPS is awaiting the

return of input power."

::= { upsWellKnownAlarms 21 }

upsAlarmShutdownPending OBJECT-IDENTITY

STATUS current

DESCRIPTION

"A upsShutdownAfterDelay countdown is underway."

::= { upsWellKnownAlarms 22 }

upsAlarmShutdownImminent OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The UPS will turn off power to the load in less than

5 seconds; this may be either a timed shutdown or a

low battery shutdown."

::= { upsWellKnownAlarms 23 }

upsAlarmTestInProgress OBJECT-IDENTITY

STATUS current

DESCRIPTION

"A test is in progress, as initiated and indicated by

the Test Group. Tests initiated via other

implementation-specific mechanisms can indicate the

presence of the testing in the alarm table, if

desired, via a OBJECT-IDENTITY macro in the MIB

document specific to that implementation and are

outside the scope of this OBJECT-IDENTITY."

::= { upsWellKnownAlarms 24 }

--

-- The Test Group

--

upsTest OBJECT IDENTIFIER ::= { upsObjects 7 }

upsTestId OBJECT-TYPE

SYNTAX OBJECT IDENTIFIER

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The test is named by an OBJECT IDENTIFIER which

allows a standard mechanism for the initiation of

tests, including the well known tests identified in

this document as well as those introduced by a

particular implementation, i.e., as documented in the

private enterprise MIB definition for the device.

Setting this variable initiates the named test. Sets

to this variable require the presence of

upsTestSpinLock in the same SNMP message.

The set request will be rejected with an appropriate

error message if the requested test cannot be

performed, including attempts to start a test when

another test is already in progress. The status of

the current or last test is maintained in

upsTestResultsSummary. Tests in progress may be

aborted by setting the upsTestId variable to

upsTestAbortTestInProgress.

Read operations return the value of the name of the

test in progress if a test is in progress or the name

of the last test performed if no test is in progress,

unless no test has been run, in which case the well

known value upsTestNoTestsInitiated is returned."

::= { upsTest 1 }

-- see [6] for more information on the semantics of objects with

-- syntax of TestAndIncr

upsTestSpinLock OBJECT-TYPE

SYNTAX TestAndIncr

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"A spin lock on the test subsystem. The spinlock is

used as follows.

Before starting a test, a manager-station should make

sure that a test is not in progress as follows:

try_again:

get (upsTestSpinLock)

while (upsTestResultsSummary == inProgress) {

/* loop while a test is running for another

manager */

short delay

get (upsTestSpinLock)

}

lock_value = upsTestSpinLock

/* no test in progress, start the test */

set (upsTestSpinLock = lock_value, upsTestId =

requested_test)

if (error_index == 1) { /* (upsTestSpinLock

failed) */

/* if problem is not access control, then

some other manager slipped in ahead of us

*/

goto try_again

}

if (error_index == 2) { /* (upsTestId) */

/* cannot perform the test */

give up

}

/* test started ok */

/* wait for test completion by polling

upsTestResultsSummary */

get (upsTestSpinLock, upsTestResultsSummary,

upsTestResultsDetail)

while (upsTestResultsSummary == inProgress) {

short delay

get (upsTestSpinLock, upsTestResultsSummary,

upsTestResultsDetail)

}

/* when test completes, retrieve any additional

test results */

/* if upsTestSpinLock == lock_value + 1, then

these are our test */

/* results (as opposed to another manager's */

The initial value of upsTestSpinLock at agent

initialization shall

be 1."

::= { upsTest 2 }

upsTestResultsSummary OBJECT-TYPE

SYNTAX INTEGER {

donePass(1),

doneWarning(2),

doneError(3),

aborted(4),

inProgress(5),

noTestsInitiated(6)

}

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The results of the current or last UPS diagnostics

test performed. The values for donePass(1),

doneWarning(2), and doneError(3) indicate that the

test completed either successfully, with a warning, or

with an error, respectively. The value aborted(4) is

returned for tests which are aborted by setting the

value of upsTestId to upsTestAbortTestInProgress.

Tests which have not yet concluded are indicated by

inProgress(5). The value noTestsInitiated(6)

indicates that no previous test results are available,

such as is the case when no tests have been run since

the last reinitialization of the network management

subsystem and the system has no provision for non-

volatile storage of test results."

::= { upsTest 3 }

upsTestResultsDetail OBJECT-TYPE

SYNTAX DisplayString (SIZE (0..255))

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"Additional information about upsTestResultsSummary.

If no additional information available, a zero length

string is returned."

::= { upsTest 4 }

upsTestStartTime OBJECT-TYPE

SYNTAX TimeStamp

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The value of sysUpTime at the time the test in

progress was initiated, or, if no test is in progress,

the time the previous test was initiated. If the

value of upsTestResultsSummary is noTestsInitiated(6),

upsTestStartTime has the value 0."

::= { upsTest 5 }

upsTestElapsedTime OBJECT-TYPE

SYNTAX TimeInterval

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The amount of time, in TimeTicks, since the test in

progress was initiated, or, if no test is in progress,

the previous test took to complete. If the value of

upsTestResultsSummary is noTestsInitiated(6),

upsTestElapsedTime has the value 0."

::= { upsTest 6 }

--

-- Well known tests.

--

upsWellKnownTests OBJECT IDENTIFIER ::= { upsTest 7 }

upsTestNoTestsInitiated OBJECT-IDENTITY

STATUS current

DESCRIPTION

"No tests have been initiated and no test is in

progress."

::= { upsWellKnownTests 1 }

upsTestAbortTestInProgress OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The test in progress is to be aborted / the test in

progress was aborted."

::= { upsWellKnownTests 2 }

upsTestGeneralSystemsTest OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The manufacturer's standard test of UPS device

systems."

::= { upsWellKnownTests 3 }

upsTestQuickBatteryTest OBJECT-IDENTITY

STATUS current

DESCRIPTION

"A test that is sufficient to determine if the battery

needs replacement."

::= { upsWellKnownTests 4 }

upsTestDeepBatteryCalibration OBJECT-IDENTITY

STATUS current

DESCRIPTION

"The system is placed on battery to a discharge level,

set by the manufacturer, sufficient to determine

battery replacement and battery run-time with a high

degree of confidence. WARNING: this test will leave

the battery in a low charge state and will require

time for recharging to a level sufficient to provide

normal battery duration for the protected load."

::= { upsWellKnownTests 5 }

--

-- The Control group.

--

upsControl OBJECT IDENTIFIER ::= { upsObjects 8 }

upsShutdownType OBJECT-TYPE

SYNTAX INTEGER {

output(1),

system(2)

}

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"This object determines the nature of the action to be

taken at the time when the countdown of the

upsShutdownAfterDelay and upsRebootWithDuration

objects reaches zero.

Setting this object to output(1) indicates that

shutdown requests should cause only the output of the

UPS to turn off. Setting this object to system(2)

indicates that shutdown requests will cause the entire

UPS system to turn off."

::= { upsControl 1 }

upsShutdownAfterDelay OBJECT-TYPE

SYNTAX INTEGER (-1..2147483648)

UNITS "seconds"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"Setting this object will shutdown (i.e., turn off)

either the UPS output or the UPS system (as determined

by the value of upsShutdownType at the time of

shutdown) after the indicated number of seconds, or

less if the UPS batteries become depleted. Setting

this object to 0 will cause the shutdown to occur

immediately. Setting this object to -1 will abort the

countdown. If the system is already in the desired

state at the time the countdown reaches 0, then

nothing will happen. That is, there is no additional

action at that time if upsShutdownType = system and

the system is already off. Similarly, there is no

additional action at that time if upsShutdownType =

output and the output is already off. When read,

upsShutdownAfterDelay will return the number of

seconds remaining until shutdown, or -1 if no shutdown

countdown is in effect. On some systems, if the agent

is restarted while a shutdown countdown is in effect,

the countdown may be aborted. Sets to this object

override any upsShutdownAfterDelay already in effect."

::= { upsControl 2 }

upsStartupAfterDelay OBJECT-TYPE

SYNTAX INTEGER (-1..2147483648)

UNITS "seconds"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"Setting this object will start the output after the

indicated number of seconds, including starting the

UPS, if necessary. Setting this object to 0 will

cause the startup to occur immediately. Setting this

object to -1 will abort the countdown. If the output

is already on at the time the countdown reaches 0,

then nothing will happen. Sets to this object

override the effect of any upsStartupAfterDelay

countdown or upsRebootWithDuration countdown in

progress. When read, upsStartupAfterDelay will return

the number of seconds until startup, or -1 if no

startup countdown is in effect. If the countdown

expires during a utility failure, the startup shall

not occur until the utility power is restored. On

some systems, if the agent is restarted while a

startup countdown is in effect, the countdown is

aborted."

::= { upsControl 3 }

upsRebootWithDuration OBJECT-TYPE

SYNTAX INTEGER (-1..300)

UNITS "seconds"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"Setting this object will immediately shutdown (i.e.,

turn off) either the UPS output or the UPS system (as

determined by the value of upsShutdownType at the time

of shutdown) for a period equal to the indicated

number of seconds, after which time the output will be

started, including starting the UPS, if necessary. If

the number of seconds required to perform the request

is greater than the requested duration, then the

requested shutdown and startup cycle shall be

performed in the minimum time possible, but in no case

shall this require more than the requested duration

plus 60 seconds. When read, upsRebootWithDuration

shall return the number of seconds remaining in the

countdown, or -1 if no countdown is in progress. If

the startup should occur during a utility failure, the

startup shall not occur until the utility power is

restored."

::= { upsControl 4 }

upsAutoRestart OBJECT-TYPE

SYNTAX INTEGER {

on(1),

off(2)

}

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"Setting this object to 'on' will cause the UPS system

to restart after a shutdown if the shutdown occurred

during a power loss as a result of either a

upsShutdownAfterDelay or an internal battery depleted

condition. Setting this object to 'off' will prevent

the UPS system from restarting after a shutdown until

an operator manually or remotely explicitly restarts

it. If the UPS is in a startup or reboot countdown,

then the UPS will not restart until that delay has

been satisfied."

::= { upsControl 5 }

--

-- The Configuration group.

--

upsConfig OBJECT IDENTIFIER ::= { upsObjects 9 }

upsConfigInputVoltage OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The magnitude of the nominal input voltage. On those

systems which support read-write access to this

object, if there is an attempt to set this variable to

a value that is not supported, the request must be

rejected and the agent shall respond with an

appropriate error message, i.e., badValue for SNMPv1,

or inconsistentValue for SNMPv2."

::= { upsConfig 1 }

upsConfigInputFreq OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 Hertz"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The nominal input frequency. On those systems which

support read-write access to this object, if there is

an attempt to set this variable to a value that is not

supported, the request must be rejected and the agent

shall respond with an appropriate error message, i.e.,

badValue for SNMPv1, or inconsistentValue for SNMPv2."

::= { upsConfig 2 }

upsConfigOutputVoltage OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The magnitude of the nominal output voltage. On

those systems which support read-write access to this

object, if there is an attempt to set this variable to

a value that is not supported, the request must be

rejected and the agent shall respond with an

appropriate error message, i.e., badValue for SNMPv1,

or inconsistentValue for SNMPv2."

::= { upsConfig 3 }

upsConfigOutputFreq OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "0.1 Hertz"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The nominal output frequency. On those systems which

support read-write access to this object, if there is

an attempt to set this variable to a value that is not

supported, the request must be rejected and the agent

shall respond with an appropriate error message, i.e.,

badValue for SNMPv1, or inconsistentValue for SNMPv2."

::= { upsConfig 4 }

upsConfigOutputVA OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "Volt-Amps"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The magnitude of the nominal Volt-Amp rating."

::= { upsConfig 5 }

upsConfigOutputPower OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "Watts"

MAX-ACCESS read-only

STATUS current

DESCRIPTION

"The magnitude of the nominal true power rating."

::= { upsConfig 6 }

upsConfigLowBattTime OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "minutes"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The value of upsEstimatedMinutesRemaining at which a

lowBattery condition is declared. For agents which

support only discrete (discontinuous) values, then the

agent shall round up to the next supported value. If

the requested value is larger than the largest

supported value, then the largest supported value

shall be selected."

::= { upsConfig 7 }

upsConfigAudibleStatus OBJECT-TYPE

SYNTAX INTEGER {

disabled(1),

enabled(2),

muted(3)

}

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The requested state of the audible alarm. When in

the disabled state, the audible alarm should never

sound. The enabled state is self-describing. Setting

this object to muted(3) when the audible alarm is

sounding shall temporarily silence the alarm. It will

remain muted until it would normally stop sounding and

the value returned for read operations during this

period shall equal muted(3). At the end of this

period, the value shall revert to enabled(2). Writes

of the value muted(3) when the audible alarm is not

sounding shall be accepted but otherwise shall have no

effect."

::= { upsConfig 8 }

upsConfigLowVoltageTransferPoint OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The minimum input line voltage allowed before the UPS

system transfers to battery backup."

::= { upsConfig 9 }

upsConfigHighVoltageTransferPoint OBJECT-TYPE

SYNTAX NonNegativeInteger

UNITS "RMS Volts"

MAX-ACCESS read-write

STATUS current

DESCRIPTION

"The maximum line voltage allowed before the UPS

system transfers to battery backup."

::= { upsConfig 10 }

--

-- notifications, i.e., traps

--

upsTraps OBJECT IDENTIFIER ::= { upsMIB 2 }

-- This section defines the well-known notifications sent by

-- UPS agents.

-- Care must be taken to insure that no particular notification

-- is sent to a single receiving entity more often than once

-- every five seconds.

upsTrapOnBattery NOTIFICATION-TYPE

OBJECTS { upsEstimatedMinutesRemaining, upsSecondsOnBattery,

upsConfigLowBattTime }

STATUS current

DESCRIPTION

"The UPS is operating on battery power. This trap is

persistent and is resent at one minute intervals until

the UPS either turns off or is no longer running on

battery."

::= { upsTraps 1 }

upsTrapTestCompleted NOTIFICATION-TYPE

OBJECTS { upsTestId, upsTestSpinLock,

upsTestResultsSummary, upsTestResultsDetail,

upsTestStartTime, upsTestElapsedTime }

STATUS current

DESCRIPTION

"This trap is sent upon completion of a UPS diagnostic

test."

::= { upsTraps 2 }

upsTrapAlarmEntryAdded NOTIFICATION-TYPE

OBJECTS { upsAlarmId, upsAlarmDescr }

STATUS current

DESCRIPTION

"This trap is sent each time an alarm is inserted into

to the alarm table. It is sent on the insertion of

all alarms except for upsAlarmOnBattery and

upsAlarmTestInProgress."

::= { upsTraps 3 }

upsTrapAlarmEntryRemoved NOTIFICATION-TYPE

OBJECTS { upsAlarmId, upsAlarmDescr }

STATUS current

DESCRIPTION

"This trap is sent each time an alarm is removed from

the alarm table. It is sent on the removal of all

alarms except for upsAlarmTestInProgress."

::= { upsTraps 4 }

--

-- conformance information

--

upsConformance OBJECT IDENTIFIER ::= { upsMIB 3 }

upsCompliances OBJECT IDENTIFIER ::= { upsConformance 1 }

--

-- compliance statements

--

upsSubsetCompliance MODULE-COMPLIANCE

STATUS current

DESCRIPTION

"The compliance statement for UPSs that only support

the two-contact communication protocol."

MODULE -- this module

MANDATORY-GROUPS { upsSubsetIdentGroup,

upsSubsetBatteryGroup, upsSubsetInputGroup,

upsSubsetOutputGroup, upsSubsetAlarmGroup,

upsSubsetControlGroup, upsSubsetConfigGroup }

OBJECT upsBatteryStatus

SYNTAX INTEGER {

batteryNormal(2),

batteryLow(3)

}

DESCRIPTION

"Support of the values unknown(1) and

batteryDepleted(4) is not required."

OBJECT upsAlarmDescr

DESCRIPTION

"Support of all `well known' alarm types is not

required. The well known alarm types which must be

supported are: upsAlarmOnBattery, upsAlarmLowBattery,

upsAlarmInputBad, upsAlarmUpsOutputOff,

upsAlarmUpsSystemOff, and upsAlarmTestInProgress."

OBJECT upsOutputSource

SYNTAX INTEGER {

normal(2),

battery(4)

}

DESCRIPTION

"Support of the values other(1), none(2), bypass(4),

booster(6) and reducer(7) is not required."

OBJECT upsShutdownType

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required, i.e., compliant

systems need not support more than one shutdown type."

OBJECT upsAutoRestart

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required, i.e., compliant

systems need not support more than one restart type."

OBJECT upsConfigInputVoltage

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigInputFreq

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigOutputVoltage

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigOutputFreq

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

::= { upsCompliances 1 }

upsBasicCompliance MODULE-COMPLIANCE

STATUS current

DESCRIPTION

"The compliance statement for UPSs that support

full-featured functions, such as control."

MODULE -- this module

MANDATORY-GROUPS { upsBasicIdentGroup,

upsBasicBatteryGroup, upsBasicInputGroup,

upsBasicOutputGroup, upsBasicAlarmGroup,

upsBasicTestGroup, upsBasicControlGroup,

upsBasicConfigGroup }

OBJECT upsAlarmDescr

DESCRIPTION

"Support of all `well known' alarm types is not

required. The well known alarm types which must be

supported are: upsAlarmOnBattery, upsAlarmLowBattery,

upsAlarmDepletedBattery, upsAlarmTempBad,

upsAlarmInputBad, upsAlarmOutputOverload,

upsAlarmOnBypass, upsAlarmBypassBad,

upsAlarmOutputOffAsRequested,

upsAlarmUpsOffAsRequested, upsAlarmUpsOutputOff,

upsAlarmUpsSystemOff, upsAlarmGeneralFault,

upsAlarmDiagnosticTestFailed,

upsAlarmCommunicationsLost, upsAlarmShutdownPending,

and upsAlarmTestInProgress."

OBJECT upsTestId

DESCRIPTION

"Support of all `well known' test types is not

required. If no tests are supported, then the only

well known test type which must be supported is

upsTestNoTestsInitiated."

OBJECT upsOutputSource

SYNTAX INTEGER {

normal(2),

battery(4)

}

DESCRIPTION

"Support of the values other(1), none(2), bypass(4),

booster(6) and reducer(7) is not required."

GROUP upsBasicBypassGroup

DESCRIPTION

"The upsBasicBypassGroup is only required for UPSs

that have a Bypass present."

OBJECT upsShutdownType

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required, i.e., compliant

systems need not support more than one shutdown type."

OBJECT upsAutoRestart

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required, i.e., compliant

systems need not support more than one restart type."

OBJECT upsConfigInputVoltage

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigInputFreq

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigOutputVoltage

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigOutputFreq

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigLowBattTime

DESCRIPTION

"Implementation of all possible values may be oNerous

for some systems. Consequently, not all possible

values must be supported. However, at least two

different manufacturer-selected values must be

supported."

::= { upsCompliances 2 }

upsFullCompliance MODULE-COMPLIANCE

STATUS current

DESCRIPTION

"The compliance statement for UPSs that support

advanced full-featured functions."

MODULE -- this module

MANDATORY-GROUPS { upsFullIdentGroup, upsFullBatteryGroup,

upsFullInputGroup, upsFullOutputGroup,

upsFullAlarmGroup, upsFullTestGroup,

upsFullControlGroup, upsFullConfigGroup }

OBJECT upsAlarmDescr

DESCRIPTION

"Support of all `well known' alarm types is not

required. The well known alarm types which must be

supported are: upsAlarmBatteryBad, upsAlarmOnBattery,

upsAlarmLowBattery, upsAlarmDepletedBattery,

upsAlarmTempBad, upsAlarmInputBad, upsAlarmOnBypass,

upsAlarmBypassBad, upsAlarmOutputOffAsRequested,

upsAlarmUpsOffAsRequested, upsAlarmUpsOutputOff,

upsAlarmUpsSystemOff, upsAlarmGeneralFault,

upsAlarmDiagnosticTestFailed,

upsAlarmCommunicationsLost, upsAlarmShutdownPending,

and upsAlarmTestInProgress."

OBJECT upsTestId

DESCRIPTION

"Support of all `well known' test types is not

required. The well known test types which must be

supported are: upsTestNoTestsInitiated,

upsTestGeneralSystemsTest, and

upsTestQuickBatteryTest."

OBJECT upsOutputSource

SYNTAX INTEGER {

normal(2),

battery(4)

}

DESCRIPTION

"Support of the values other(1), none(2), bypass(4),

booster(6) and reducer(7) is not required."

GROUP upsFullBypassGroup

DESCRIPTION

"The upsFullBypassGroup is only required for UPSs that

have a Bypass present."

OBJECT upsShutdownType

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required, i.e., compliant

systems need not support more than one shutdown type."

OBJECT upsAutoRestart

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required, i.e., compliant

systems need not support more than one restart type."

OBJECT upsConfigInputVoltage

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigInputFreq

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigOutputVoltage

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigOutputFreq

MIN-ACCESS read-only

DESCRIPTION

"Read-write access is not required."

OBJECT upsConfigLowBattTime

DESCRIPTION

"Implementation of all possible values may be onerous

for some systems. Consequently, not all possible

values must be supported. However, at least two

different manufacturer-selected values must be

supported."

::= { upsCompliances 3 }

--

-- units of conformance

--

-- summary at a glance:

-- subset basic adv

--upsIdentManufacturer x x x

--upsIdentModel x x x

--upsIdentUPSSoftwareVersion x x

--upsIdentAgentSoftwareVersion x x x

--upsIdentName x x x

--upsIdentAttachedDevices x x

--

--upsBatteryStatus x x x notes

--upsSecondsOnBattery x x x

--upsEstimatedMinutesRemaining x

--upsEstimatedChargeRemaining x

--upsBatteryVoltage

--upsBatteryCurrent

--upsBatteryTemperature

--

--upsInputLineBads x x x

--upsInputNumLines x x

--upsInputFrequency x x

--upsInputVoltage x x

--upsInputCurrent

--upsInputTruePower

--

--upsOutputSource x x x notes

--upsOutputFrequency x x

--upsOutputNumLines x x

--upsOutputVoltage x x

--upsOutputCurrent x

--upsOutputPower x

--upsOutputPercentLoad x

--

--

--upsBypassFrequency x x notes

--upsBypassNumLines x x

--upsBypassVoltage x x

--upsBypassCurrent

--upsBypassPower

--

--

--upsAlarmsPresent x x x

--upsAlarmDescr x x x notes

--upsAlarmTime x x x

--

--upsTestId x x notes

--upsTestSpinLock x x

--upsTestResultsSummary x x

--upsTestResultsDetail x x

--upsTestStartTime x x

--upsTestElapsedTime x x

--

--upsShutdownType x x x notes

--upsShutdownAfterDelay x x x

--upsStartupAfterDelay x x

--upsRebootWithDuration x x

--upsAutoRestart x x x notes

--

--upsConfigInputVoltage x x x notes

--upsConfigInputFreq x x x notes

--upsConfigOutputVoltage x x x notes

--upsConfigOutputFreq x x x notes

--upsConfigOutputVA x x x

--upsConfigOutputPower x x x

--upsConfigLowBattTime x x notes

--upsConfigAudibleStatus x x

--upsConfigLowVoltageTransferPoint

--upsConfigHighVoltageTransferPoint

-- units of conformance

upsGroups OBJECT IDENTIFIER ::= { upsConformance 2 }

upsSubsetGroups OBJECT IDENTIFIER ::= { upsGroups 1 }

upsSubsetIdentGroup OBJECT-GROUP

OBJECTS { upsIdentManufacturer, upsIdentModel,

upsIdentAgentSoftwareVersion, upsIdentName,

upsIdentAttachedDevices }

STATUS current

DESCRIPTION

"The upsSubsetIdentGroup defines objects which are

common across all UPSs which meet subset compliance.

Most devices which conform to the upsSubsetIdentGroup

will provide access to these objects via a proxy

agent. If the proxy agent is compatible with multiple

UPS types, configuration of the proxy agent will

require specifying some of these values, either

individually, or as a group (perhaps through a table

lookup mechanism based on the UPS model number)."

::= { upsSubsetGroups 1 }

upsSubsetBatteryGroup OBJECT-GROUP

OBJECTS { upsBatteryStatus, upsSecondsOnBattery }

STATUS current

DESCRIPTION

"The upsSubsetBatteryGroup defines the objects that

are common to battery groups of two-contact UPSs."

::= { upsSubsetGroups 2 }

upsSubsetInputGroup OBJECT-GROUP

OBJECTS { upsInputLineBads }

STATUS current

DESCRIPTION

"The upsSubsetInputGroup defines the objects that are

common to the Input groups of two-contact UPSs."

::= { upsSubsetGroups 3 }

upsSubsetOutputGroup OBJECT-GROUP

OBJECTS { upsOutputSource }

STATUS current

DESCRIPTION

"The upsSubsetOutputGroup defines the objects that are

common to the Output groups of two-contact UPSs."

::= { upsSubsetGroups 4 }

-- { upsSubsetGroups 5 } is reserved for

-- future use (upsSubsetBypassGroup)

upsSubsetAlarmGroup OBJECT-GROUP

OBJECTS { upsAlarmsPresent, upsAlarmDescr, upsAlarmTime }

STATUS current

DESCRIPTION

"The upsSubsetAlarmGroup defines the objects that are

common to the Alarm groups of two-contact UPSs."

::= { upsSubsetGroups 6 }

-- { upsSubsetGroups 7 } is reserved for

-- future use (upsSubsetTestGroup)

upsSubsetControlGroup OBJECT-GROUP

OBJECTS { upsShutdownType, upsShutdownAfterDelay,

upsAutoRestart }

STATUS current

DESCRIPTION

"The upsSubsetControlGroup defines the objects that

are common to the Control groups of two-contact UPSs."

::= { upsSubsetGroups 8 }

upsSubsetConfigGroup OBJECT-GROUP

OBJECTS { upsConfigInputVoltage, upsConfigInputFreq,

upsConfigOutputVoltage, upsConfigOutputFreq,

upsConfigOutputVA, upsConfigOutputPower }

STATUS current

DESCRIPTION

"The upsSubsetConfigGroup defines the objects that are

common to the Config groups of two-contact UPSs."

::= { upsSubsetGroups 9 }

upsBasicGroups OBJECT IDENTIFIER ::= { upsGroups 2 }

upsBasicIdentGroup OBJECT-GROUP

OBJECTS { upsIdentManufacturer, upsIdentModel,

upsIdentUPSSoftwareVersion,

upsIdentAgentSoftwareVersion, upsIdentName }

STATUS current

DESCRIPTION

"The upsBasicIdentGroup defines objects which are

common to the Ident group of compliant UPSs which

support basic functions."

::= { upsBasicGroups 1 }

upsBasicBatteryGroup OBJECT-GROUP

OBJECTS { upsBatteryStatus, upsSecondsOnBattery }

STATUS current

DESCRIPTION

"The upsBasicBatteryGroup defines the objects that are

common to the battery groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 2 }

upsBasicInputGroup OBJECT-GROUP

OBJECTS { upsInputLineBads, upsInputNumLines,

upsInputFrequency, upsInputVoltage }

STATUS current

DESCRIPTION

"The upsBasicInputGroup defines the objects that are

common to the Input groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 3 }

upsBasicOutputGroup OBJECT-GROUP

OBJECTS { upsOutputSource, upsOutputFrequency,

upsOutputNumLines, upsOutputVoltage }

STATUS current

DESCRIPTION

"The upsBasicOutputGroup defines the objects that are

common to the Output groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 4 }

upsBasicBypassGroup OBJECT-GROUP

OBJECTS { upsBypassFrequency, upsBypassNumLines,

upsBypassVoltage }

STATUS current

DESCRIPTION

"The upsBasicBypassGroup defines the objects that are

common to the Bypass groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 5 }

upsBasicAlarmGroup OBJECT-GROUP

OBJECTS { upsAlarmsPresent, upsAlarmDescr, upsAlarmTime }

STATUS current

DESCRIPTION

"The upsBasicAlarmGroup defines the objects that are

common to the Alarm groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 6 }

upsBasicTestGroup OBJECT-GROUP

OBJECTS { upsTestId, upsTestSpinLock,

upsTestResultsSummary, upsTestResultsDetail,

upsTestStartTime, upsTestElapsedTime }

STATUS current

DESCRIPTION

"The upsBasicTestGroup defines the objects that are

common to the Test groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 7 }

upsBasicControlGroup OBJECT-GROUP

OBJECTS { upsShutdownType, upsShutdownAfterDelay,

upsStartupAfterDelay, upsRebootWithDuration,

upsAutoRestart }

STATUS current

DESCRIPTION

"The upsBasicControlGroup defines the objects that are

common to the Control groups of compliant UPSs which

support basic functions."

::= { upsBasicGroups 8 }

upsBasicConfigGroup OBJECT-GROUP

OBJECTS { upsConfigInputVoltage, upsConfigInputFreq,

upsConfigOutputVoltage, upsConfigOutputFreq,

upsConfigOutputVA, upsConfigOutputPower,

upsConfigLowBattTime, upsConfigAudibleStatus }

STATUS current

DESCRIPTION

"The upsBasicConfigGroup defines the objects that are

common to the Config groups of UPSs which support

basic functions."

::= { upsBasicGroups 9 }

upsFullGroups OBJECT IDENTIFIER ::= { upsGroups 3 }

upsFullIdentGroup OBJECT-GROUP

OBJECTS { upsIdentManufacturer, upsIdentModel,

upsIdentUPSSoftwareVersion,

upsIdentAgentSoftwareVersion, upsIdentName,

upsIdentAttachedDevices }

STATUS current

DESCRIPTION

"The upsFullIdentGroup defines objects which are

common to the Ident group of fully compliant UPSs."

::= { upsFullGroups 1 }

upsFullBatteryGroup OBJECT-GROUP

OBJECTS { upsBatteryStatus, upsSecondsOnBattery,

upsEstimatedMinutesRemaining,

upsEstimatedChargeRemaining }

STATUS current

DESCRIPTION

"The upsFullBatteryGroup defines the objects that are

common to the battery groups of fully compliant UPSs."

::= { upsFullGroups 2 }

upsFullInputGroup OBJECT-GROUP

OBJECTS { upsInputLineBads, upsInputNumLines,

upsInputFrequency, upsInputVoltage }

STATUS current

DESCRIPTION

"The upsFullInputGroup defines the objects that are

common to the Input groups of fully compliant UPSs."

::= { upsFullGroups 3 }

upsFullOutputGroup OBJECT-GROUP

OBJECTS { upsOutputSource, upsOutputFrequency,

upsOutputNumLines, upsOutputVoltage,

upsOutputCurrent, upsOutputPower,

upsOutputPercentLoad }

STATUS current

DESCRIPTION

"The upsFullOutputGroup defines the objects that are

common to the Output groups of fully compliant UPSs."

::= { upsFullGroups 4 }

upsFullBypassGroup OBJECT-GROUP

OBJECTS { upsBypassFrequency, upsBypassNumLines,

upsBypassVoltage }

STATUS current

DESCRIPTION

"The upsFullBypassGroup defines the objects that are

common to the Bypass groups of fully compliant UPSs."

::= { upsFullGroups 5 }

upsFullAlarmGroup OBJECT-GROUP

OBJECTS { upsAlarmsPresent, upsAlarmDescr, upsAlarmTime }

STATUS current

DESCRIPTION

"The upsFullAlarmGroup defines the objects that are

common to the Alarm groups of fully compliant UPSs."

::= { upsFullGroups 6 }

upsFullTestGroup OBJECT-GROUP

OBJECTS { upsTestId, upsTestSpinLock,

upsTestResultsSummary, upsTestResultsDetail,

upsTestStartTime, upsTestElapsedTime }

STATUS current

DESCRIPTION

"The upsFullTestGroup defines the objects that are

common to the Test groups of fully compliant UPSs."

::= { upsFullGroups 7 }

upsFullControlGroup OBJECT-GROUP

OBJECTS { upsShutdownType, upsShutdownAfterDelay,

upsStartupAfterDelay, upsRebootWithDuration,

upsAutoRestart }

STATUS current

DESCRIPTION

"The upsFullControlGroup defines the objects that are

common to the Control groups of fully compliant UPSs."

::= { upsFullGroups 8 }

upsFullConfigGroup OBJECT-GROUP

OBJECTS { upsConfigInputVoltage, upsConfigInputFreq,

upsConfigOutputVoltage, upsConfigOutputFreq,

upsConfigOutputVA, upsConfigOutputPower,

upsConfigLowBattTime, upsConfigAudibleStatus }

STATUS current

DESCRIPTION

"The upsFullConfigGroup defines the objects that are

common to the Config groups of fully compliant UPSs."

::= { upsFullGroups 9 }

END

5. Acknowledgements

The UPS MIB represents the combined work of the IETF UPS MIB Working

Group, with particular, substantial authorship contributions from:

Mike Davison

Fibercom, Inc.

Ray Wasson

Consultant

Roger Draper

Liebert Corporation

Ken Key

SNMP Research, Incorporated

Pete Yoest

American Power Conversion

Doug Rademacher

American Power Conversion

Ron Pitt

Network Security Systems, Inc

Terry Zumwalt

International Power Machines

Lawren Markle

Tripp Lite

Bill Elliot

ONEAC

Tom Brennan

Exide Electronics

Brian Young

Best Power Technology

6. References

[1] Case, J., Fedor, M., Schoffstall, M., and J. Davin, "Simple

Network Management Protocol", STD 15, RFC1157, SNMP Research,

Inc., Performance Systems International, Performance Systems

International, MIT Laboratory for Computer Science, May 1990.

[2] Case, J., McCloghrie, K., Rose, M., and S. Waldbusser, "Protocol

Operations for Version 2 of the Simple Network Management

Protocol (SNMPv2)", RFC1448, SNMP Research, Inc., Hughes LAN

Systems, Dover Beach Consulting, Inc., Carnegie Mellon

University, April 1993.

[3] McCloghrie, K., and M. Rose, Editors, "Management Information

Base for Network Management of TCP/IP-based internets: MIB-II",

STD 17, RFC1213, Hughes LAN Systems, Performance Systems

International, March 1991.

[4] Case, J., McCloghrie, K., Rose, M., and S. Waldbusser, "Structure

of Management Information for Version 2 of the Simple Network

Management Protocol (SNMPv2)", RFC1442, SNMP Research, Inc.,

Hughes LAN Systems, Dover Beach Consulting, Inc., Carnegie Mellon

University, April 1993.

[5] Case, J., McCloghrie, K., Rose, M., and S. Waldbusser,

"Conformance Statements for Version 2 of the Simple Network

Management Protocol (SNMPv2)", RFC1444, SNMP Research, Inc.,

Hughes LAN Systems, Dover Beach Consulting, Inc., Carnegie Mellon

University, April, 1993.

[6] Case, J., McCloghrie, K., Rose, M., and S. Waldbusser, "Textual

Conventions for Version 2 of the Simple Network Management

Protocol (SNMPv2)", RFC1443, SNMP Research, Inc., Hughes LAN

Systems, Dover Beach Consulting, Inc., Carnegie Mellon

University, April 1993.

7. Security Considerations

Security issues are not discussed in this memo.

8. Author's Address

Jeffrey D. Case, Ph.D.

SNMP Research, Incorporated

3001 Kimberlin Heights Road

Knoxville, Tennessee 37920

Phone: (615) 573-1434

 
 
 
免责声明:本文为网络用户发布,其观点仅代表作者个人观点,与本站无关,本站仅提供信息存储服务。文中陈述内容未经本站证实,其真实性、完整性、及时性本站不作任何保证或承诺,请读者仅作参考,并请自行核实相关内容。
2023年上半年GDP全球前十五强
 百态   2023-10-24
美众议院议长启动对拜登的弹劾调查
 百态   2023-09-13
上海、济南、武汉等多地出现不明坠落物
 探索   2023-09-06
印度或要将国名改为“巴拉特”
 百态   2023-09-06
男子为女友送行,买票不登机被捕
 百态   2023-08-20
手机地震预警功能怎么开?
 干货   2023-08-06
女子4年卖2套房花700多万做美容:不但没变美脸,面部还出现变形
 百态   2023-08-04
住户一楼被水淹 还冲来8头猪
 百态   2023-07-31
女子体内爬出大量瓜子状活虫
 百态   2023-07-25
地球连续35年收到神秘规律性信号,网友:不要回答!
 探索   2023-07-21
全球镓价格本周大涨27%
 探索   2023-07-09
钱都流向了那些不缺钱的人,苦都留给了能吃苦的人
 探索   2023-07-02
倩女手游刀客魅者强控制(强混乱强眩晕强睡眠)和对应控制抗性的关系
 百态   2020-08-20
美国5月9日最新疫情:美国确诊人数突破131万
 百态   2020-05-09
荷兰政府宣布将集体辞职
 干货   2020-04-30
倩女幽魂手游师徒任务情义春秋猜成语答案逍遥观:鹏程万里
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案神机营:射石饮羽
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案昆仑山:拔刀相助
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案天工阁:鬼斧神工
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案丝路古道:单枪匹马
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案镇郊荒野:与虎谋皮
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案镇郊荒野:李代桃僵
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案镇郊荒野:指鹿为马
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案金陵:小鸟依人
 干货   2019-11-12
倩女幽魂手游师徒任务情义春秋猜成语答案金陵:千金买邻
 干货   2019-11-12
 
推荐阅读
 
 
 
>>返回首頁<<
 
靜靜地坐在廢墟上,四周的荒凉一望無際,忽然覺得,淒涼也很美
© 2005- 王朝網路 版權所有